A bit of a stretch for this group but the experts seem to be here.
Our building wants to install seperate meters for our power in part to
mitigate the expence of the condo's power bill.
The building is 208V but most abbliances are 220. I know for example
that my mother can boil a pot of water in about 5 minutes on her 220
service and 22 stove (not new or efficient) but on my 208 service and
220 stove it takes much longer.
Q: Am I paying more to boil a pot of water or not?
Some say that the meter doesn't work that way and that if I had a 12V
service and 24 hours to boil the water it would be the same as 208 for
much less time..
Help me out here folks...
Beamer Smith
I have spent most of my money on women and beer. The rest I just
wasted...
E. Lee Dickinson
02-02-2007, 03:55 PM
"Beamer Smith" <beamer@imhavingan.org> wrote in message
news:jcc5s2lj3fi2hu3jek410b0roi234hk8rp@4ax.com...
>A bit of a stretch for this group but the experts seem to be here.
> Our building wants to install seperate meters for our power in part to
> mitigate the expence of the condo's power bill.
> The building is 208V but most abbliances are 220. I know for example
> that my mother can boil a pot of water in about 5 minutes on her 220
> service and 22 stove (not new or efficient) but on my 208 service and
> 220 stove it takes much longer.
> Q: Am I paying more to boil a pot of water or not?
> Some say that the meter doesn't work that way and that if I had a 12V
> service and 24 hours to boil the water it would be the same as 208 for
> much less time..
> Help me out here folks...
My thought is that it takes a fixed amount of total energy input to boil a
pot of water. Wether a low input is applied over a long time versus a higher
input over a shorter time doesn't make much difference.
However, this may not be true, when you think it down to the extremes. In
your example, it is likely the 12v input would NEVER boil the water, as the
thermal loss would be greater (or at least equal) to the thermal input. So
you could run the 12v heater in perpetuity and boil nothing but dollars.
So I suppose a higher temperature is probably more effecient. Measurable in
dollars? That would be an interesting experiment.
B Fuhrmann
03-02-2007, 12:25 AM
"Beamer Smith" wrote ...
>A bit of a stretch for this group but the experts seem to be here.
> Our building wants to install seperate meters for our power in part to
> mitigate the expence of the condo's power bill.
> The building is 208V but most abbliances are 220. I know for example
> that my mother can boil a pot of water in about 5 minutes on her 220
> service and 22 stove (not new or efficient) but on my 208 service and
> 220 stove it takes much longer.
> Q: Am I paying more to boil a pot of water or not?
No. You pay for power by the Killowatt Hour (KWH). 1 Killowatt Hour = 1
Kilowatt hour regardless of the voltage that it is delivered at or the how
fast you use the energy.
You pay the same for using:
4.55 Amps @ 220 volts (1 KW) for 1 hour,
4.81 Amps @ 208 Volts (1 KW) for 1 hour,
83.3 Amps @ 12 Volts (1 KW) for 1 hour,
.455 Amps @ 220 volts (0.1 KW) for 10 hours,
.481 Amps @ 208 Volts (0.1 KW) for 10 hours,
.833 Amps @ 12 Volts (0.1 KW) for 10 hours.
Watt Hours are a measure of engergy used, like calories.
1 watt hour = 860.42 calories
Heating a cup of water from 72 def F to 212 deg F (but not boiling it) takes
33,122 calories or 0.385 KWH.
That ignores any heat that is wasted in the process (heating things near the
stove) and does not include turning any water into steam (actually boiling
it).
The effect on your stove of running 208 instead of 220 volts is that the
heating elements will not draw energy as fast. Looking at the example
above, a resistive heater that is designed to run at 1KW @ 220V will have a
48.4 Ohm resistance. Using that same 48.4 Ohm heating element on 208 volts
gives us a 4.30 Amps or 0.895 KW.
To use the same energy that the 220V heating element uses in an hour, you
would need to run the 208V stove for 1 hour and 7 minutes.
The only limitation is that your highest heat is not quite as high.
The payback you get for that is that the heating element will last a little
longer because it is not running as hot.
--
Bill Fuhrmann
....
Marc_F_Hult
03-02-2007, 04:23 AM
On Thu, 01 Feb 2007 22:54:35 -0500, Beamer Smith <beamer@imhavingan.org>
wrote in message <jcc5s2lj3fi2hu3jek410b0roi234hk8rp@4ax.com>:
>A bit of a stretch for this group but the experts seem to be here.
>Our building wants to install seperate meters for our power in part to
>mitigate the expence of the condo's power bill.
>The building is 208V but most abbliances are 220. I know for example
>that my mother can boil a pot of water in about 5 minutes on her 220
>service and 22 stove (not new or efficient) but on my 208 service and
>220 stove it takes much longer.
>Q: Am I paying more to boil a pot of water or not?
>Some say that the meter doesn't work that way and that if I had a 12V
>service and 24 hours to boil the water it would be the same as 208 for
>much less time..
>Help me out here folks...
>
Bill and Lee are correct in the assertion that you pay for watts not volts.
But that's not the whole answer. The Tea-kettle question is an classic
example of an energy budget which is parallel/similar to a mass balance
problem.).
Think of it first with the close analogy of a kettle with a leak being
filled with water (mass balance):
RateWaterIn - RateWaterLeaked = Change in amount of water stored in kettle
Note whether you ever fill the kettle depends on BOTH rates. Too large a
leak (hole) and the kettle never fills.
For making a kettle boil, the budget is:
For temp < 212F
Heat In - Heat Out = Change in Heat stored in kettle
Heat Out ("lost") is a function of:
Time,
K, Thermal conductivity of the kettle material
Temperature difference between kettle and environment
So if you reduce Time, you reduce heat loss.
So the 12 volt element may never get the water in an uninsulated kettle to
boil, the 208 is less efficient than 220 volts and the most efficient is
INSTANTLY applying enough heat to boil the water because there is not time
to lose any heat.
If you reduce thermal conductivity of the kettle walls (i.e, insulate the
kettle as is done with some electric kettles) you reduce heat loss.
Alternatively, you could raise the room temperature to 211 F to minimize
the delta T heat loss. Hard on the heating bill among other things...
.... Marc
Marc_F_Hult
www.ECOntrol.org
Marc_F_Hult
03-02-2007, 04:23 AM
On Fri, 02 Feb 2007 09:48:17 -0500, Marc_F_Hult
<MFHult@nothydrologistnot.com> wrote in message
<hth6s21mh57ld2ik6jnvj8aefqaav007ik@4ax.com>:
>On Thu, 01 Feb 2007 22:54:35 -0500, Beamer Smith <beamer@imhavingan.org>
>wrote in message <jcc5s2lj3fi2hu3jek410b0roi234hk8rp@4ax.com>:
>
>>A bit of a stretch for this group but the experts seem to be here.
>>Our building wants to install seperate meters for our power in part to
>>mitigate the expence of the condo's power bill.
>>The building is 208V but most abbliances are 220. I know for example
>>that my mother can boil a pot of water in about 5 minutes on her 220
>>service and 22 stove (not new or efficient) but on my 208 service and
>>220 stove it takes much longer.
>>Q: Am I paying more to boil a pot of water or not?
>>Some say that the meter doesn't work that way and that if I had a 12V
>>service and 24 hours to boil the water it would be the same as 208 for
>>much less time..
>>Help me out here folks...
>>
>
>Bill and Lee are correct in the assertion that you pay for watts not
volts.
>
>But that's not the whole answer. The Tea-kettle question is an classic
>example of an energy budget which is parallel/similar to a mass balance
>problem.).
>
>Think of it first with the close analogy of a kettle with a leak being
>filled with water (mass balance):
>
>RateWaterIn - RateWaterLeaked = Change in amount of water stored in kettle
XXXX^^^^^^ XXXX^^^^^^^^^^^
WaterIn WaterLeaked
>
>Note whether you ever fill the kettle depends on BOTH rates. Too large a
>leak (hole) and the kettle never fills.
>
>For making a kettle boil, the budget is:
>For temp < 212F
>
> Heat In - Heat Out = Change in Heat stored in kettle
>
>Heat Out ("lost") is a function of:
>
> Time,
> K, Thermal conductivity of the kettle material
> Temperature difference between kettle and environment
>
>
>So if you reduce Time, you reduce heat loss.
>
>So the 12 volt element may never get the water in an uninsulated kettle to
>boil, the 208 is less efficient than 220 volts and the most efficient is
>INSTANTLY applying enough heat to boil the water because there is not time
>to lose any heat.
>
>If you reduce thermal conductivity of the kettle walls (i.e, insulate the
>kettle as is done with some electric kettles) you reduce heat loss.
>
>Alternatively, you could raise the room temperature to 211 F to minimize
>the delta T heat loss. Hard on the heating bill among other things...
>
>... Marc
>Marc_F_Hult
>www.ECOntrol.org
I ought to read my messages before I hit the carriage return ....
L^3 (amount) not L^3/t (rate), in LHS of the first equation. See
correction.
Marc
Marc_F_Hult
www.ECOntrol.org
Robert L Bass
03-02-2007, 08:21 AM
> I ought to read my messages before I hit the carriage return ....
> L^3 (amount) not L^3/t (rate), in LHS of the first equation. See
> correction.
It must be entertaining trying to cook with an oven mitt on one hand and an engineering calculator in the other. :^)
--
Regards,
Robert L Bass
=============================>
Bass Home Electronics
941-866-1100
4883 Fallcrest Circle
Sarasota · Florida · 34233
http://www.bassburglaralarms.com
=============================>
Beamer Smith
17-02-2007, 02:12 PM
Marc_F_Hult <MFHult@nothydrologistnot.com> wrote:
>On Thu, 01 Feb 2007 22:54:35 -0500, Beamer Smith <beamer@imhavingan.org>
>wrote in message <jcc5s2lj3fi2hu3jek410b0roi234hk8rp@4ax.com>:
>
>>A bit of a stretch for this group but the experts seem to be here.
>>Our building wants to install seperate meters for our power in part to
>>mitigate the expence of the condo's power bill.
>>The building is 208V but most abbliances are 220. I know for example
>>that my mother can boil a pot of water in about 5 minutes on her 220
>>service and 22 stove (not new or efficient) but on my 208 service and
>>220 stove it takes much longer.
>>Q: Am I paying more to boil a pot of water or not?
>>Some say that the meter doesn't work that way and that if I had a 12V
>>service and 24 hours to boil the water it would be the same as 208 for
>>much less time..
>>Help me out here folks...
>>
>
>Bill and Lee are correct in the assertion that you pay for watts not volts.
>
>But that's not the whole answer. The Tea-kettle question is an classic
>example of an energy budget which is parallel/similar to a mass balance
>problem.).
>
>Think of it first with the close analogy of a kettle with a leak being
>filled with water (mass balance):
>
>RateWaterIn - RateWaterLeaked = Change in amount of water stored in kettle
>
>Note whether you ever fill the kettle depends on BOTH rates. Too large a
>leak (hole) and the kettle never fills.
>
>For making a kettle boil, the budget is:
>For temp < 212F
>
> Heat In - Heat Out = Change in Heat stored in kettle
>
>Heat Out ("lost") is a function of:
>
> Time,
> K, Thermal conductivity of the kettle material
> Temperature difference between kettle and environment
>
>
>So if you reduce Time, you reduce heat loss.
>
>So the 12 volt element may never get the water in an uninsulated kettle to
>boil, the 208 is less efficient than 220 volts and the most efficient is
>INSTANTLY applying enough heat to boil the water because there is not time
>to lose any heat.
>
>If you reduce thermal conductivity of the kettle walls (i.e, insulate the
>kettle as is done with some electric kettles) you reduce heat loss.
>
>Alternatively, you could raise the room temperature to 211 F to minimize
>the delta T heat loss. Hard on the heating bill among other things...
>
>... Marc
>Marc_F_Hult
>www.ECOntrol.org
Um...OK...
While my condo is Very hot (being on the top floor contributes to
that) I'm not sure I can get the boiler to give me 211F <snicker>
So the upshot to all this is that I'm not paying any more to boil a
208 pot of water than my mom is moiling a 220 pot of water (all other
things being equal.. ) Or at least microscopicly so.
Now all I need to do is solve why I'm usually getting 195 or so volts
to that stove outlet
(damned aluminum wiring)
Thanks folks
Beamer